Hello I have a few questions. I'm running new wiring from house to sugarhouse to accommodate for the RO and other stuff I will be running.
Items include
Air blower for fire box auf
Filter press small 7"
RO with a 5hp 220 hp pump and a 2 hp 220 feed pump.
Lights, radio Eco..

It's apprx 130' from panel in house to panel in sugarhouse.

What size wire should I be looking for? And is alluimiun good?
Reply With Quote
  #2  
Old October 2nd, 2014, 08:27 PM
Banned
Producer


 
Location: Parker Colorado/Jacksonport wisconsin
Join Date: Oct 2011
Journals: 1
Photos: 6
Posts: 7,188
Thanked 843 Times
  View my photos   Read my journals
Default

Will it be underground. I would put it in Grey conduit and go with at least 4 Gauge. Do you have the space for it in you house panel. Most house loops are aluminum so yea its fine. You will need 2 lines a 2 grounds.
Reply With Quote
  #3  
Old October 2nd, 2014, 08:57 PM
Kevin Sargent's Avatar
2013 Calendar Contest Winner
Researcher


 
Location: Newport, NH
Number of Taps: 2
Join Date: Dec 2011
Photos: 18
Posts: 1,273
Thanked 332 Times
  View my photos  
Default

Best to find out what your TOTAL AMP LOAD will be and add extra 20% to that for start up electrical draw and as you said 130' of distance and look on electrical chart to tell you what size cable you would need. Guessing 60amp min on main sugar house panel and 30 amp for Lapierre 5hp RO. And 15amp on lights/outlet and 15 on other accessories.

Again figure out max amps needed=might be 100 at SH/ I don't know your needs but you need to figure that out? Vac pump at SH? Better make it 100 but some older houses are only 100amp to start with.
__________________
Is this thing working or what?
World's Sweetest Maple Tree - YouTube
Reply With Quote
  #4  
Old October 2nd, 2014, 09:14 PM
Member
Producer


 
Location: Maine
Number of Taps: 400
Join Date: Dec 2011
Posts: 472
Thanked 18 Times
 
Default

I agree 100 would be best I have 200 at my sugar house and in the room were I have a water pump, vac pump and ro I have a 100 amp sub panel so there's not a million feeds run over to that one room.
__________________
350 taps
Reply With Quote
  #5  
Old October 2nd, 2014, 09:17 PM
Member
Producer
 
Location: Berlin, PA
Number of Taps: 2300
Join Date: Jan 2012
Posts: 144
Thanked 15 Times
 
Default

What size panel in sugar house? I would recommend 100 amp panel with aluminum feeding it.#2 aluminum for 3 conductors and a #6 aluminum for a ground. There might be a multiplex cable you can buy for this. Then like Haynes said place wire in conduit.
__________________
30"x12' evaporator
H2O 3 post ro
2300 vacuum
Reply With Quote
  #6  
Old October 2nd, 2014, 10:00 PM
wishlist's Avatar
Contributing Member
Producer
 
Location: Lennon, Michigan
Number of Taps: 900
Join Date: Feb 2012
Classified Ads: 2
Photos: 3
Posts: 1,707
Thanked 210 Times
  View my photos   View my ads  
Default

Quote:
Originally Posted by Haynes Forest Products View Post
Will it be underground. I would put it in Grey conduit and go with at least 4 Gauge. Do you have the space for it in you house panel. Most house loops are aluminum so yea its fine. You will need 2 lines a 2 grounds.
Quote:
Originally Posted by mountain man maple View Post
What size panel in sugar house? I would recommend 100 amp panel with aluminum feeding it.#2 aluminum for 3 conductors and a #6 aluminum for a ground. There might be a multiplex cable you can buy for this. Then like Haynes said place wire in conduit.
No, no, no!

Jp, you said your gonna have a sub panel in the sugarhouse. In that case then you only run 2 hots and a neutral from your house to the panel. Bond the neutral to ground in the panel and then you must drive in a ground rod . I would run conduit and copper.
Reply With Quote
  #7  
Old October 2nd, 2014, 11:41 PM
3rdgen.maple's Avatar
Sugarbush.Info Administrator
Manufacturer
 
Location: Altmar, NY
Number of Taps: 2000
Join Date: Oct 2011
Journals: 9
Photos: 29
Posts: 6,355
Thanked 961 Times
  View my photos   Read my journals
Default

If you plan on doing this yourself I would check your insurance policy. If by chance something goes wrong and they find out this work was not done by a certified electrician or inspected you might be SOL. Better safe than sorry and ask.
Reply With Quote
  #8  
Old October 2nd, 2014, 11:49 PM
wishlist's Avatar
Contributing Member
Producer
 
Location: Lennon, Michigan
Number of Taps: 900
Join Date: Feb 2012
Classified Ads: 2
Photos: 3
Posts: 1,707
Thanked 210 Times
  View my photos   View my ads  
Default

Quote:
Originally Posted by 3rdgen.maple View Post
If you plan on doing this yourself I would check your insurance policy. If by chance something goes wrong and they find out this work was not done by a certified electrician or inspected you might be SOL. Better safe than sorry and ask.
That's always a good idea. In Michigan a homeowner can legally do electrical work for themselves. Inspections vary from townships to city's on what needs a permit and what doesn't.
Reply With Quote
  #9  
Old October 3rd, 2014, 10:18 PM
Member
Producer


 
Location: Maine
Number of Taps: 400
Join Date: Dec 2011
Posts: 472
Thanked 18 Times
 
Default

You really should check with a local electrician. here in Maine you are suppose to run a seperate grounds and neutrals back to the panel from the sub panel because there could be a difference in impedance and having the way you describe wishlist could POSSIBLY not saying it will result in a dangerous situation.
__________________
350 taps
Reply With Quote
The Following User Says Thank You to 500592 For This Post:
Haynes Forest Products (October 3rd, 2014)
  #10  
Old October 3rd, 2014, 11:50 PM
Banned
Producer


 
Location: Parker Colorado/Jacksonport wisconsin
Join Date: Oct 2011
Journals: 1
Photos: 6
Posts: 7,188
Thanked 843 Times
  View my photos   Read my journals
Default

Thank you